I cant connect to Digi unless RS485 device is momentarily disconnected when I initiate TCP/IP

0 votes
asked Aug 15, 2014 in Portserver TS by Mark Vandersteeg New to the Community (1 point)

Please log in or register to answer this question.

2 Answers

0 votes
What is the error/behavior seen when trying to connect?

What does the "who" command show when attempting to connect?

What does "display ports" show when trying to connect?

Is grounding wired on the cable (SGND and Chassis)?

You might want to confirm cabling:

http://smax.digi.com/kbase/kbaseedit.aspx?kbid=3489
answered Aug 18, 2014 by userid0 Veteran of the Digi Community (2,158 points)
0 votes
the issue turned out to be that the device i was connecting the Digi unit to defaulted on the baud rate when power was disconnected.
Thanks for the replies...I tried all your suggestions and it led me to the solution.
answered Aug 25, 2014 by Mark Vandersteeg New to the Community (1 point)
...